Card 9 - ZONE_CONVECTION Thermal Convection Zone Definition
This optional card specifies the parameters and options for defining a boundary condition that creates a convection coupling between a group of selected elements and a fluid environment.
Parameters: KODE, N1, T1, T2, T3
KODE
KODE is the code ZONE_CONVECTION (or 92)
N1
N1 is the ZONE_CONVECTION card ID. Cards with the same ID reference the same Thermal Convection Zone.
T1
T1 specifies the type of parameter for the thermal convection zone.
T1 = FACTOR
T1 = FACTOR (or 11) An area correction factor is specified. This
input corrects the convective area.
- If the area correction factor is constant, then its value is specified in T2.
- If the area correction factor is table dependent, then T2 is a table multiplier and T3 has the form Tn (e.g., T25) where n is a table number referencing the TABTYPE and FIELDTYPE cards. The dependent variable on the TABTYPE card must be NUMBER.
- If the area correction factor is calculated using an expression, then T2 is an expression multiplier and T3 has the form En (e.g., E25) where n is an expression number referencing the EXPRESSION card.
T1 = HTC
T1 = HTC (or 5) A heat transfer coefficient for
the convection between the selected elements and the fluid environment is
specified.
- If the heat transfer coefficient is constant, then its value is specified in T2.
- If the heat transfer coefficient is table dependent, then T2 is a table multiplier and T3 has the form Tn (e.g., T25) where n is a table number referencing the TABTYPE or FIELDTYPE cards. The dependent variable on the TABTYPE card must be COND.
- If the heat transfer coefficient is calculated using an expression, then T2 is an expression multiplier and T3 has the form En (e.g., E25) where n is an expression number referencing the EXPRESSION card.
T1 = HTFL
T1 = HTFL (or 8) A heat flux is specified for the
thermal convection zone.
- If the heat flux is constant, then its value is specified in T2.
- If the heat flux is table dependent, then T2 is a table multiplier and T3 has the form Tn (e.g., T25) where n is a table number referencing the TABTYPE or FIELDTYPE cards. The dependent variable on the TABTYPE card must be HTFL.
- If the heat flux is calculated using an expression, then T2 is an expression multiplier and T3 has the form En (e.g., E25) where n is an expression number referencing the EXPRESSION card.
T1 = MAT
T1 = MAT (or 2) The material ID of the primary fluid environment is
specified in T2.
T1 = MAT_LIST
T1 = MAT_LIST (or 7) Additional fluid materials are
defined. The ID of the MATLIST card, which lists these additional fluid materials,
is specified in T2.
T1 = NAME
T1 = NAME (or 6) The load name is specified in
T2.
T1 = PRESSURE
T1 = PRESSURE (or 3) A pressure is specified for the thermal
convection zone.
- If the pressure is constant, then its value is specified in T2.
- If the pressure is table dependent, then T2 is a table multiplier and T3 has the form Tn (e.g., T25) where n is a table number referencing the TABTYPE or FIELDTYPE cards. The dependent variable on the TABTYPE card must be PTOTAL.
- If the pressure is calculated using an expression, then T2 is an expression multiplier and T3 has the form En (e.g., E25) where n is an expression number referencing the EXPRESSION card.
T1 = ROT_FX
T1 = ROT_FX (or 6) The thermal convection zone
temperatures are corrected for rotational effects. The ID of the referenced ROT_FX
cards is specified in T2.
T1 = SELECTION
T1 = SELECTION (or 1) The thermal convection zone
is applied to a selection of elements that are represented by the group name T2.
T1 = TEMPERATURE
T1 = TEMPERATURE (or 4) A temperature is specified for the fluid
environment.
- If the temperature is constant, then its value is specified in T2.
- If the temperature is table dependent, then T2 is a table multiplier and T3 has the form Tn (e.g., T25) where n is a table number referencing the TABTYPE or FIELDTYPE cards. The dependent variable on the TABTYPE card must be TEMP.
- If the temperature is calculated using an expression, then T2 is an expression multiplier and T3 has the form En (e.g., E25) where n is an expression number referencing the EXPRESSION card.
T1 = THICK
T1 = THICK (or 10) The area for internal edges is specified. This
input is used to compute the convective area when the Thermal Convection Zone is
applied to internal edges.
- If thicknesses are subtracted, then
T2 = SUB. - If thicknesses are added, then
T2 = ADD.
T1 = OVERRIDE
T1 = OVERRIDE (or 12) An area override is specified. This input
overrides the convective area.
- If the area override is constant, then its value is specified in T2.
- If the area override is table dependent, then T2 is a table multiplier and T3 has the form Tn (e.g., T25) where n is a table number referencing the TABTYPE and FIELDTYPE cards. The dependent variable on the TABTYPE card must be NUMBER.
- If the area override is calculated using an expression, then T2 is an expression multiplier and T3 has the form En (e.g., E25) where n is an expression number referencing the EXPRESSION card.
T1 = ADIABATIC_WALL_TEMP_FOR_HTC
T1 = ADIABATIC_WALL_TEMP_FOR_HTC (or 14) Specifies how an adiabatic
wall temperature for heat transfer calculations is defined in T2.
T2 = TEMPERATURE: Specifies a value for an adiabatic wall temperature.T2 = AUTOMATIC: An adiabatic wall temperature value is computed by the thermal solver. IfT2 = AUTOMATIC, the thermal solver computes the adiabatic wall temperature and uses it in heat transfer calculations as follows: where:
- Ts is the static temperature.
- RF = Pr1/2film is the recovery factor that is computed by the thermal solver, or can be specified in RECOVERY_FACTOR.
Pris the Prandtl number calculated at .- vrel = abs(u - vϕ) is the relative tangential velocity, where u is a wall velocity and vϕ is a swirl velocity.
- Cp is the specific heat at the fluid temperature Tfilm.
T1 = WALL_TEMP
T1 = WALL_TEMP (or 16) Specifies a value for an adiabatic wall
temperature in T2.
- If the adiabatic wall temperature is constant, then its value is specified in
T2. - If it is table dependent, then
T2is a table multiplier andT3has the formTn(e.g.,T25) wherenis a table number referencing TABTYPE or FIELDTYPE cards. The dependent variable on the TABTYPE card must be NUMBER. - If the adiabatic wall temperature is calculated using an expression, then
T2is an expression multiplier andT3has the formEn(e.g.,E25) wherenis an expression number referencing EXPRESSION card.
T1 = RECOVERY_FACTOR
T1 = RECOVERY_FACTOR (or 15) Specifies a value for the recovery
factor, which is used to compute the adiabatic wall temperature, in
T2.
- If the recovery factor is constant, then its value is specified in
T2. - If it is table dependent, then
T2is a table multiplier andT3has the formTn(e.g.,T25) wherenis a table number referencing TABTYPE or FIELDTYPE cards. The dependent variable on the TABTYPE card must be NUMBER. - If the recovery factor is calculated using an expression, then
T2is an expression multiplier andT3has the formEn(e.g.,E25) wherenis an expression number referencing EXPRESSION card.
Code example
$ Thermal Convecting Zone(1)
NAME2 Thermal Thermal Convecting Zone(1)
NAME Thermal 328 345 1
ZONE_CONVECTION 1 SELECTION "Thermal Convecting Zone(1)"
ZONE_CONVECTION 1 MAT 2
ZONE_CONVECTION 1 PRESSURE 2.000000E+03
ZONE_CONVECTION 1 TEMPERATURE 1.0 T16
ZONE_CONVECTION 1 HTC 1.0 T8
ZONE_CONVECTION 1 HTFL 1.0 T8
ZONE_CONVECTION 1 ROT_FX 1
