Card 6u - DIURNAL4 Solar Heating Modeling Request
This optional card defines the solar flux calculation options for the diurnal solar heating modeling request.
Parameter | Value | Description |
---|---|---|
DIURNAL4 |
DIURNAL4 (or 64) | Mnemonic |
ID |
Integer | Request ID number |
FLUXOPT |
NOATT | No atmospheric attenuation |
ATT | Atmospheric attenuation occurs and is evaluated with the atmospheric extinction coefficient method | |
TABLE | VAL1 is a solar flux table number |
|
TURB | Atmospheric attenuation occurs and is evaluated with the altitude and turbidity method | |
VAL1 |
Real | Apparent solar radiation value if FLUXOPT=ATT , and
the solar flux value for FLUXOPT=TURB |
Integer | Solar flux table number if FLUXOPT = TABLE |
|
VAL2 |
Real value | Atmospheric extinction coefficient if FLUXOPT=ATT
and turbidity factor for FLUXOPT=TURB . Otherwise, it is
unused |
VAL3 |
Real value | Clearness factor if FLUXOPT=ATT and clearness index
if FLUXOPT=ATT or FLUXOPT=TURB .
Otherwise, it is unused |
VAL4 |
Real value | Diffuse sky radiation factor if FLUXOPT=ATT .
Otherwise, it is unused |
VAL5 |
Real value | Albedo value if FLUXOPT=ATT or
FLUXOPT=TURB . Otherwise, it is unused |
VAL6 |
FACTOR | Controls the overcast conditions method. VAL3 is a
clearness factor |
INDEX | Controls the overcast conditions method. VAL3 is a
clearness index |
|
0 or blank | If FLUXOPT=NOATT or
FLUXOPT=TABLE |
FLUXOPT
FLUXOPT
specifies the type of solar flux calculation option.
VAL1
VAL1
can be:
- The value of the solar flux outside the atmosphere if
FLUXOPT=NOATT
orFLUXOPT=TURB
. - The table number of the time-dependent solar flux value defined in Card 9
TABTYPE
Card forFLUXOPT=TABLE
. - The “apparent solar flux” defined in the ASHRAE Fundamentals Handbook, Edition 1997, pp. 29.17 for
FLUXOPT=ATT
.
If a table-dependent solar flux is defined, the dependent parameter in the TABTYPE Card must be QNODE, and the independent parameter must be TIME.
VAL2
VAL2
is the atmospheric extinction coefficient value if FLUXOPT = ATT
. The direct normal irradiation at the Earth’s surface of a plate normal to the sun is defined to be:
where β is the angle between the horizon and the sun vector is found in the table of ASHRAE Handbook, HVAC Applications 1995, SI edition, p. 30.2.
VAL2
is the Linke turbidity factor if FLUXOPT = TURB
. The direct normal irradiation, at the Earth’s surface of a plate normal to the sun, is defined as:
where:
- m is the relative optical air mass.
- δR(m) is the Rayleigh optical thickness at air mass m is found in Suri, Marcel, and Jaroslav Hofierk, Transactions in GIS 8.2, 2004, p. 175-190.
VAL3
VAL3
is the clearness factor value if FLUXOPT = FACTOR
, otherwise it is blank or 0.
The clearness factor is the ratio between the actual clear day direction radiation intensity at a specific location, and the intensity calculated for the standard atmosphere at the same location and date. The reference for clearness factor is found in ASHRAE Handbook, 1995, HVAC Applications, pp. 30.5. Clearness values > 1 indicate a very dry and clear sky, for example, a sky at high altitudes. Conversely, clearness values < 1 indicate very hazy and humid conditions.
VAL3
is the clearness index value if FLUXOPT = INDEX
. The clearness index is the ratio of radiation on a horizontal surface to the extraterrestrial radiation. The clearness index is employed to estimate solar radiation under overcast conditions using the Solar Energy Research Institute method found in Maxwell, E.L., 1987, Solar Energy Research Institute, United States.
VAL4
VAL4
is the diffuse sky radiation factor if FLUXOPT = ATT
, otherwise it should be blank or 0.
This is the ratio of the diffuse solar flux originating from the sky incident upon a horizontal plate to the direct attenuated solar flux incident upon a plate normal to the sun vector. (cf table 1 ASHRAE Handbook, 1995, HVAC Applications, p30.2)
VAL5
VAL5
is the albedo value if FLUXOPT = ATT
or FLUXOPT = TURB
, otherwise, it is blank or 0.
Albedo is the fraction of the solar radiation reflected from the nearby ground.
VAL6
VAL6
specifies the type of clearness values that are defined for VAL3
.
Code example
DIURNAL4 3 ATT 1.188116E+03 1.559929E-01 1.000000E+00 7.115684E-02 3.060000E-01 FACTOR
DIURNAL4 3 NOATT 1100.0
DIURNAL4 3 TABLE 10